Multiplus 12/3000 & Lynx Distributor

I am connecting the Multiplus to a Lynx distributor. The manual states that the recommended cable size is 2 x 50mm and the recommended fuse size is 400A. Oceanflex 50mm is rated at 345A so I am assuming that I would install two x 200A fuses in the distributor.

Is this correct?


MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
JohnC avatar image
JohnC answered ·

Yes, that should be fine.