Quattro with Venus & Genset

Hello Team, we have following configuration:

2 x Quattro 48V/10000 with a Venus and a 30kWh BYD battery bank. The inverters are configured as a split phase system with a 30kVA diesel genset. The system is set up to start the generator automatically at some preset levels. During our test we have noticed that the system cuts off the genset abruptly instead of sending the turn-off signal and allowing the genset to cool down. We have replaced the Venus because we thought that the Venus might be sending a double signal to the generator controller which would cause an immediate shutdown. But this did not fix the problem. Does anyone have any other idea what we could test?

GeneratorVenus GX - VGXSOC
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Durmus

The Victron system only sends a 'generator run' signal, it is up to the generator control system to control a disconnect and run-down time. (same when starting generator)

2 |3000