question

wudycool avatar image
wudycool asked

after ess update no feed-in and overcharging

Hello i updated the ess and now no feed in anymore.

feed in is enabled in the victron panel. i dont understand why it is not working anymore...

can someone tell me how to truble shoot this? i am happy to give more informaiton :D

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
wudycool avatar image
wudycool answered ·

hello, i found the problem.

somehow the quattro 8000 was set to off in the ccgx and this coused the strange behavior. the leds on the quattro showed it was on normal. so i did not thought about that and it took me some time to trouble shoot.

thank you anyhow for the quick response.

case closed.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @wudycool,

Please confirm you are running the current latest firmware on all devices on the system. It is the first thing to check in a troublesome system.

Also, can you please tell me the grid code used, and the grid code settings.

Also, can you please check the AC input current (A), and power (W), and make sure the power factor is what it should be.

2 |3000