Using Hex Protocol asked SmartSolar MPPT 100/20 for capabilities register. Sent command was:
:74001000D
And response was:
:740010075DE0D0AA3
Extracting data is 75DE0D0A which converted to binary is:
0111 0101 1101 1110 0000 1101 0000 1010
Bit 0 (First bit) contains 0 meaning no Load Output present.
How come that? SmartSolar MPPT 100/20 does have Load Output present.
Could this be the reason why when I configure Load Output as User defined algorithm 1: off < 12.5V, on > 13.3V the battery voltage drops under 12.5 volts for 10+ minutes (I have seen 12.2 volts) and the charger doesn't disconnect the Load Output.
It is important to mention that I can set Load output to off manually in the app and the load output disconnects. The same, if I set to on it connects.
With Load Output I am just driving a relay (with protection diode) which consumes only 0.089 amps.