question

user0815 avatar image
user0815 asked

2 off grid systems AC coupling?

Hello

I would like to connect 2 Victron off grid systems via AC.

System 1 (1 x MP2 5000) is in a small workshop at the back of the property and is rarely used. The battery is often fully charged. This means that energy is lost. A 3 x 4mm² cable, approx. 30-35 meters long, goes to the workshop. The battery is charged via MPPT charge controller and 2 Hoymiles inverters.

System 2 (3 x MP2 5000 in parallel).

My plan:

The AC In from system 1 is connected to the AC Out from system 2. When the battery of system 1 is full, the MP2 starts feeding into the "grid" of system 2. If the battery of system 2 is full, the frequency is increased and the feed-in of system 1 is stopped.

At 53Hz, the Hoymiles no longer feed in. Does this also apply to the DC side feed of the MP2?

Am I making a mistake somewhere and should I pay attention to something else?

Regards

Paul

------------------------

Hallo

Ich möchte 2 Victron Inselanlagen per AC koppeln.

Anlage 1 (1 x MP2 5000) ist in einer kleinen Werkstatt, hinten auf dem Grundstück und wird selten genutzt. Der Akku ist oft vollgeladen. Somit geht Energie verloren. Zu der Werkstatt geht ein 3 x 4mm² Kabel, ca. 30-35 Meter lang. Die Batterie wird über MPPT Laderegler und 2 Hoymiles Inverter geladen.

Anlage 2 (3 x MP2 5000 parallel).

Mein Plan:

Der AC In von der Anlage 1 wird auf AC Out von der Anlage 2 aufgeschaltet. Wenn die Batterie der Anlage 1 voll ist, fängt der MP2 in das "Netz" der Anlage 2 einzuspeisen. Sollte die Batterie der Anlage 2 voll sein, wird die Frequenz angehoben und somit die Einspeisung der Anlage 1 gestoppt.

Bei 53Hz speisen die Hoymiles nicht mehr ein. Gilt das auch für die DC Seitige Einspeisung des MP2?

Habe ich irgendwo einen Denkfehler und sollte ich noch etwas beachten?

Gruß

Paul

ac coupling
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@user0815

DC mppts do not respond to frequency shifting. You need another way to stop/control feedback.

FYI this is not an officially supported set up.

0 Likes 0 ·
user0815 avatar image user0815 Alexandra ♦ commented ·

DC MMPT are controlled and stopped by the MP2/Cerbo GX

0 Likes 0 ·
1 Answer
user0815 avatar image
user0815 answered ·

It works very well.

1000180497.jpg

1000180498.jpg


1000180497.jpg (255.5 KiB)
1000180498.jpg (250.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

AC-coupling and the Factor 1.0 rule


AC-coupled PV with Fronius PV Inverters



Additional resources still need to be added for this topic