question

ianw530 avatar image
ianw530 asked

Bmv 712 smart relay no longer switches current when operated

Initially the 712 would switch current to the NC relay teminal as per settings i made in the setup, related to the target battery hi and li voltage values set. Yesterday altough i can hear the internal relay working ok, no voltage or current change seems to be occurring at the relay terminal s , and the 12v supply is checking ok

BMV Battery Monitor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
kevgermany avatar image
kevgermany answered ·

Please check with the seller for service test/repair

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pwfarnell avatar image
pwfarnell answered ·

What load were you switching with the relay.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ianw530 avatar image
ianw530 answered ·

under 2 A , separate 12 v relay

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pwfarnell avatar image pwfarnell commented ·

Quite easy to burn out the contacts when driving another relay due to the high current that is generated when the relay is turned off. See

https://victron.discourse.group/t/using-inverter-mppt-gx-device-programmable-relays-with-higher-current-inductive-or-capacitive-loads/99

1 Like 1 ·
klim8skeptic avatar image klim8skeptic ♦ commented ·
@Ianw530 Snubber diode fitted?
0 Likes 0 ·