jeroen13 avatar image
jeroen13 asked

Input current limit keeps jumping back

Hi, I have 3x MPII 5000 in three phase configuration and everything seems to be working fine except the input current limit. I used VEconfig to set the input current limit to 23A on each inverter and disabled overruled by remote. But when I check the console on the cerbo and open the multiplus it says 6A. This morning I saw that grid meter was showing 1.8kW of usage due to washingmachine so I check why the ESS was not supplying more power to compensate this. Then saw the 6A current limit, so I downloaded the configuration files from the mutltis and all 3 showed 23A limit.

I'm on firmware version 551, anyone and idea what is happing ?


Multiplus-IIcurrent limitinput current
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
jeroen13 avatar image
jeroen13 answered ·

I found out that it is the peak shaving function which was set to 6A import limit which adjusted the current limit on the MPII on AC-IN. I expected that the peak shave function would help keeping my grid meter at max 6A import but not limit the MP when more load is needed.