Settings for Tesla 24V 240Ah battery connected to Victron MultiPlus 24/3000/70-16

Hello, what settings do i use to configure a New battery type setting in VE configure in the tab "charger" for a Tesla 24V 240Ah battery connected to Victron MultiPlus 24/3000/70-16? Thanks, Steven

VEConfigure 3
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @Steven2309

This depends on the type of BMS you are using, usually set the charger to lithium, and use safe levels (like 24v), if you use a CANbus BMS (preferred) this will send the correct charging voltages and current limit to the system.

Make sure your bms can disconnect the battery by means of a shunt-trip or relay.

0 Likes 0 ·
1 Answer
steven2309 avatar image
steven2309 answered ·

I will use the Simp BMS. But not yet connected.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Please first setup your bms, that way you know for sure if the batteries are in balance.

1 Like 1 ·