Can you alter the ups configuration in a victron multiplus inverter charger 12/3000/120 to accept or iron out dirty electricity from a generator and if so how please
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Can you alter the ups configuration in a victron multiplus inverter charger 12/3000/120 to accept or iron out dirty electricity from a generator and if so how please
Hi @LesRollins,
Some of the steps you can take to work with varying grades of generator power supply are explained here in the MultiPlus Generator FAQ
None of those settings for the MultiPlus Inverter Charger will 'iron' out a bad supply though. It will either be accepted (and passed through to the loads) or rejected.
An option to 'iron' out a bad AC supply is to use a seperate charger, such as a Skylla, and have that connected to the DC bus. They have a very wide tolerance of generator supplies.
Then the batteries get charged from the generator, and the inverter supplies clean power to the loads.
Hi@Guy Stewart the charger system is working fine off the generator. I disabled the charger in the charger inverter and the washing machine still kept going on and off. I attached a honda eu20i to the inverter charger and that worked well but it was working at its max slightly to small. The washing machine works perfectly straight from the kipor 6.7kva but not through the inverter charger. I have read your link regarding generators and found it interesting I've tried all options that I'm personally capable of on the inverter charger but have come to the conclusion that it's just not going to accept the electricity from the kipor 6.7kva