Mppt 250/100 tr x 2

Good morning everyone, I have a problem to explain.
How is it possible that the charging algorithm exactly the absorption every day is skipped by my two mppt smart solar 250/100 tr.
can you help me?
A thousand thanks
MPPT ControllersMPPT SmartSolarcharger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Emanuele trusso

Yes. Enable expert mode.

Set the absorption period as fixed and set the time as low as it will go. That will disable it.

If you dont want it disabled then allow adaptive or set a fixed time.

This works only if there is no BMS control.