Charge current incorrect on Venus Venus GX

Hi there,


I have recently doubled my storage battery from Pylontech US 3000 (3.5kW) to 2x US 3000 (7.0 kW

I am running MPPT 150 / 45 Solar Controller and Multi Grid 48V/3000VA/35Amps Inverter / Charger.

The displayed charging current and Wattage seems to be that of only one battery as it does not compute up to the display on solar yield vs consumption.


I have connected the data link from Master battery Link Port "1" to Slave battery Link Port "0"

connection to Venus GX is from "CAN" port


Any advice please

MPPT ControllersSOC
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Walter Gygax

You have probably worked this out by now, but the battery dip switches need to also be configured according to the manual address system.