dbx120 avatar image
dbx120 asked

"External Transfer Switch" Generator to Multi Output

This was talked about by Victron at Intersolar this year. In an offgrid system, you can connect a generator to the output of a Multi/Quattro.

The way it seems to work is that the Generator is also wired to the input, once the Multi has synced with the Generator the relay on the closes a NO contactor connection the Generator to the Multi output.

Is there any Victron documentation on the correct implementation of this? The programmable relay assistant can be programmed to switch on when AC is available on AC1, but it doesn't explicitly state that this will only happen once the Multi has synced with this AC source.
1722906244935.png



MultiPlus Quattro Inverter ChargerGeneratortransfer switch
1722906244935.png (6.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
dbx120 avatar image
dbx120 answered ·

Answered my own question:


https://www.victronenergy.com/media/pg/MultiPlus-II_External_Transfer_Switch_application/en/configuration.html