'Day Van' Solar/Inverter System Setup

Hi,

I have a van that has an existing imverter/leisure battery setup, I have bought the following to upgrade it :


Smart Shunt

MPPT 100-20

Orion-tr NI DC-DC 12|12-30

2 x LifePo4 100Ah Ecoworthy batteries (to replace 2 x 90Ah Lead Acid)

2 x 100W Solar Panels


I have drawn up a system diagram, and just wanted advice on whether this is the correct way to setup stuff, I want to monitor as much as i can...


Thanks


system-diagram.png

MPPT SmartSolarLithium BatterySmartShuntorion-tr smart
system-diagram.png (476.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
pwfarnell avatar image
pwfarnell answered ·

@Roger Layton-Smith Functionally it looks OK, you need appropriate fusing and bus bar connection but the question appears related to functionality so I will leave that aside. The van should have a connection from the starter battery / alternator to the chassis. You will need to have a chassis to negative connection to the leisure batteries for the Orion DC-DC converter to work, both batteries need to have a common negative. This chassis to leisure battery negative needs to be attached to the system side of the shunt as shown. It could equally be a direct wire from the starter battery to the system side of the shunt if you do not want the DC-Dc charger current using the chassis.

image1.png


image1.png (344.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

roger-layton-smith avatar image
roger-layton-smith answered ·

Thanks,

I've got fuses etc. ordered, and am going to use a lynx power in for the battery connections, with the smart shunt in the middle, and a modified Lynx power in with fuses for the out...

I've ordered some copper bar to join the gap between +12 from power in and power out,
and negative from power in to shunt input - output will bolt onto power 'out' lynx)

As below:


lynx.png


lynx.png (357.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

roger-layton-smith avatar image
roger-layton-smith answered ·

Should I fuse between the power in and power out ?

2 |3000