2 x 48v 5kVA 240v in parellel - what happens if only one Quattro has AC input?

When running two Quattros in parallel mode do both AC1 inputs need to have AC present and in phase for system to operate?


For example if AC was applied to AC1 on the master only would the master engage and operate and the slave contribute to the combined output as an inverter only?


Thanks.







MultiPlus Quattro Inverter Chargerbattery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

In parallel they need input and output connected, in multiphase they can be separate:

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems