I have a system set up for 120/240v with 2 quattro 10kva. i have a diesel 12kw generator. when the AC loads go above 10000w the power assist is not able to keep the generator at a constant power. the generator pulses and eventually if the ac load is great enough, it will dissconect from the inverter.
settings are:
ups off
weak ac enabled
power assist on ( iv tried 1, 1.5, 2, 2.5, 3, 3.5 boost factor)
input limit 35A ive tried adjusting this all over its range
Im puzzled as to why the power assit will not keep the generator at its input current limit when there is higher loads. If generator is turned off the inverters will power the loads. If anyone has any insight please help!