Can a single Quattro 15000-VA control output of 2 Fronius 5kw on a/c out-1?

I have 1 Quattro 15000 VA with ESS I will be adding more pv on different roof orientation so will need to add a second fronius 5kw.

Can the Quattro control output of 2 Fronius and show them in the VRM?Cerbo gx is LAN wired.

AC PV Coupling
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@PowerGuard Electrical

The Fronius work in a network (fronius solar net) with one as a master, so you don't need to control two as individuals. They will show as combined on one tile