No data on phase 3 with ET340

Dear community

my ET340 does not show the voltage and power on phase 3. The current is correct.

Data on phase 1 and phase 2 are correct.


This is my setup:

- Venus GX

- 3 MultiPlus 5000

- BMV 700

- Li-Ion Battery

- ET340 connected via ZigBee to Venus GX

- 3 MPPT Solar chargers

- No external PV inverter (e.g. Fronius)

- The system is connected in parallel to the grid


Does anyone have an idea why there is no data on phase 3?

Thanks in advance for your support!

BR Thomas

Energy Meter
nophase3.png (55.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @IronTom16

Did you find the issue yet?
did you measure if there is voltage present at the et340?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

irontom16 avatar image irontom16 commented ·

Dear Daniel,

Yes, I found the issue and you are right with your assumption! There was a problem with the DC power supply.

The open circuit voltage of my power supply was ok but not ok when connected to the et340. Changed the power supply and now everything is working correctly.


Thanks, Thomas