Prioritze Solar charging when using "Ignore AC Input" option

Good Day,

I have a simple outcome,

Use solar to power up loads and charge batteries when available and if the loads go higher than X W amount use the grid .


Now using VS options doesn't allow you to use Assistants.


With the below I achived the following :


If the loads are > 1500W for 2seconds the Grid kicks in.

If the loads are < 800W for 2mins the battery AND solar takes over.

The battery conditions work as stated below as well.


Now the issue is :

When the grid is NOT required the system is using nearly 50% from batteries and 50% from solar (+-) .


When the batteries reach < 50% the batteries are charged from the Grid rather than the Solar.


PS : My solar array produces about 1600W


How can I maximize the use of the solar ?



MPPT Controllersbattery chargingsolarvirtual switch
1570475392558.png (47.7 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

denzel avatar image denzel commented ·

Here is an example

AC loads 316W

PV 326W

but you will see its using -186W from the battery still.

0 Likes 0 ·
1570514076763.png (45.1 KiB)
1 Answer
Elimac avatar image
Elimac answered ·

Hi,

Two small things come to mind to improve a little, not solve to 100%...

- You can set the PV Charger voltage slightly above the settings of Multi charger (100 or 200mV). But in bulk phase you might not notice much improvement...

-You can make use of AC input current limit and enable Power Assist. By doing this, if the AC is not enough to power AC loads, Power assist will "mix" Solar/battery/ and ACin. Not perfect, but might help.

I think ESS has other possibilities, but I'm no expert in ESS, I can't use it as of now.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

VE Configure/Virtual Switch

Ignore AC input using the Generator Assistant

Additional resources still need to be added for this topic

MPPT Product Page

MPPT Error codes

MPPT 150/60 up to 250/70 Manual