Multiplus II 2x120 - Error #8, PE2 Open Relay

Recently installed a MultiPlus II 2x120, 24V on a boat that has both shore power and a generator. When connected to shore power or to generator, the unit works (inverts), but Cerbo Touch Display shows a ‘#8 Ground relay test failed’ error.

When disconnected from shore (and generator not running), unit will not invert and goes into fault mode (and shows #8 error).

I have pored through the troubleshooting guide VE.Bus Error Codes [Victron Energy], to no avail.

In the course of extensive troubleshooting, wire tracing, etc., we ended up completely disconnecting all AC lines. So no AC ‘in’, no AC ‘out’. Completely physically disconnected the AC lines. Only DC battery power connected. The MP still throws the same #8 Ground relay test failed error.

The error shows the relay is ‘open’ when it should be ‘closed’ (Error: PE2 Open). This seems to correlate with why it works on shore or gen (because the relay should be open in those situations) and does not invert when on battery (when the relay should be closed).

This seems to me to indicate a hardware (relay) failure inside the MultiPlus. Does anyone have any other ideas of what to look at? I'm already planning to start a warranty return tomorrow, but.. thought I'd check here also.

processed-c2c202c4-8fa8-49f8-a7bd-1cd2a935d643.jpegprocessed-c71585be-82ee-4ad1-a87c-decaa4e9d50c.jpegprocessed-f1286557-a13c-43bf-b903-c562249bd446.jpeg

Multiplus-IIRelayGrounding
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@ColinDavis

What can happen is there is a current being detected going to ground. Or there has been a ground fault and it has welded the contact so it can't operate as it is designed to.

The fault can be related to both a hardware faliure and an install error; so be sure to check your wiring. (As in an install error {high fault current to ground or a neutral\line mix up} can cause the hardware faliure).

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

MultiPlus-II Product page 

MultiPlus-II Manual

Multiplus-II GX Online Manual

MultiPlus-II 230V Datasheet 

VE.Bus Error codes

Additional resources still need to be added for this topic

Ground, earth and electrical safety


Additional resources still need to be added for this topic