question

Guy Dahler avatar image
Guy Dahler asked

Multiplus 2 scheduled charge and UPS

Hi,


I have a multiplus 2 and Cerbo GX to manage scheduled charging from the grid between 8am and 4pm to fill my batteries and then I use battery power between (overnight).


I want to use the batteries as much as possible and I want the Multiplus to change over to the grid if the batteries get too low but I do not want it to charge the batteries until the scheduled charge time window.


Is there a way to set it to change over to the grid but not charge until the scheduled charge time from the Cerbo GX.

Multiplus-IIcerbo gx
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Duivert NL avatar image
Duivert NL answered ·

You are already using scheduled charging, sonyou can do it with that

Have a look at the ess manual page 13, it explaines how to use multiple schedules

https://www.victronenergy.com/upload/documents/Energy_Storage_System/6292-ESS_design_and_installation_manual-pdf-en.pdf

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Guy Dahler avatar image Guy Dahler commented ·

So I should set is as follows?

schedule 1: Everyday 8am to 4pm 100%

schedule 2: Everyday 4pm to 8am 20%

Then it will have a 20% margin for if the grid fails during the night.

That is how I am understanding that. Do I have that correct?

0 Likes 0 ·