Earth Fault Loop Impedance of EASY SOLAR - Multiplus 24/3000/70-50

What impedance in Ohms will the EASY SOLAR - Multiplus 24/3000/70-50 contribute to the earth fault loop impedance of the stand alone power system of which it is the sole source of power supply?

Multiplus-IIEasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Johannes Boonstra (Victron Energy Staff) avatar image
Johannes Boonstra (Victron Energy Staff) answered ·

when the unit is not powered, there is no N-E connection, so no impedance.

when the unit is powered, your measuring the transformer of the unit, and if grid is connected, also the grid itself