question

mrft avatar image
mrft asked

Easysolar AC out trips when AC in is enabled and ESS malfunctioning

Good day.

1) My Multiplus inverters in my EasySolar systems supplies the load correctly when drawing power from the solar panels and battery bank. However, when attempting to activate AC input from the grid, the 63 A RCD output breaker trips after about 30 seconds. I have measured the voltage between earth and neutral at the grid input side and there is a 0.440 v reading. This should be 0 v if I am correct. Could this be tripping the RCD and if so, can I bypass this RCD and go straight to the circuit breaker after it, which is part of the EasySolar system?

2) My ESS setup brings the low voltage light on and prevents the inverter from inverting. I have set the parameters up correctly as suggested on a previous post but still have problems.

Please help as this setup is giving me endless problems. Thank you and kind regards,

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
mrft avatar image
mrft answered ·

OK Murraynated. The inverters are inverting at the moment with no grid input available. Are you available at present to view?


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mrft avatar image
mrft answered ·

I have never shared before. Will you send me your email address so that I can send the URL?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mrft avatar image
mrft answered ·

Dear all,

In regards to the issues I have experienced with my recent setup I would like to announce that the system is up and running with no glitches at present. May I take this opportunity to thank everyone for their most valued and much appreciated inputs in helping me solve all the issues. You guys are fantastic. Thank you and warm regards.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.