ESS Fronius Throttled

Screenshot_20240628_091342_VRM.jpgScreenshot_20240628_091007_VRM.jpgScreenshot_20240628_090954_VRM.jpgScreenshot_20240628_090945_VRM.jpgScreenshot_20240628_090933_VRM.jpgScreenshot_20240630_170342_VRM.jpg

Screenshot_20240630_175843_VRM.jpg

Screenshot_20240630_181102_VRM.jpgScreenshot_20240630_181401_VRM.jpg

Hello,

I have a system that worked fine until 1 week ago. Although the batteries are discharged, the 2 Fronius are in throttled status, they are connected on AC OUTPUT of Victron. If i select to "keep batteries charged" the batteries will be charged from the grid without any problem. Also i noticed if the batteries are charged with 20A for example from PV and if i modified "pv feed in excess" to ON, the 2 Fronius will increase their power and all the pv production will go to the batteries/consumption ( from 20A to 80A example). What could be causing this?

dvcc - on

ess: AC feed in excess - OFF.

3 x Multiplus2 5000VA

2 x Fronius

6 x Pytes battery

ESSFronius
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
sean avatar image
sean answered ·

What is zero feed in power limit set to within the device settings of each Fronius ?