Is it possible - or is there an appropriate configuration - to use the Off Grid Quattro AC-out connected AC supply to (inversly) charge the batteries if no load is consuming power?
(3~ MultiPlus Quattro 8KW / AC-Supply: Inverter 230V, <1kW, 60Hz)
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Is it possible - or is there an appropriate configuration - to use the Off Grid Quattro AC-out connected AC supply to (inversly) charge the batteries if no load is consuming power?
(3~ MultiPlus Quattro 8KW / AC-Supply: Inverter 230V, <1kW, 60Hz)
I am not sure I understand, but I will try and answer.
It is never possible to connect a wave forming AC supply to the AC-out of the Quattro. You will damage something.
AC supplies can be connected to the AC-out of the Quattro if they are not wave forming. An example is an AC Solar inverter, this will not create a waveform itself, but instead will synchronise to the waveform that is created by the Quattro.
The AC outputs of multiple Quattros can be connected together in parallel, but they must be correctly configured first.
AC-coupling and the Factor 1.0 rule