Li Time Battery

I am using two 200-ah Li Time batteries in parallel with the MultiPlus-II 12/3000/120-50 2 x 120. Li Time says they have a built-in BMS. Do I still need to use a fuse between these and the Multiplus? If so, which fuse would you recommend, and what amperage?

Battery Protectmegafuse
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
kevgermany avatar image
kevgermany answered ·

Yes add a fuse. Fuse for the cable size and your loads.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pwfarnell avatar image
pwfarnell answered ·

The Multiplus manual has fusing recommendations which are good as long as you use the recommended size and number of cables.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.