Evgeniy Labunskiy asked

1 Phase Generator in 3 Phase system - option to validate

Tomorrow I have a plan to start a 3-phase MultiRS system. My problem is that I have a generator (for long-term outages) and this generator is 1 phase (yes I know I can buy 3-phase, but let me try to avoid it). I googled a lot and it looks like the following schema will work:

1. By charger Victron Skylla TG 48/50
2. Connect the charger to the bus
3. Correct 1 phase generator to charger
4. Run generator from Cerbo when SOC < 30%
5. Profit

Does this schema look correct? One question I have: it looks like these charges are dummies and cannot be controlled by Cerbo, is it ok to have such a system without actual charging control?

GeneratorMulti RS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Evgeniy Labunskiy

Yes you can. You wont be the only one to ever do it.

You can even use another inverter easier to set up and program. Then if you really want to (dig deeper) have charge control, you can set it up with node red and control it that way.

2 |3000