question

xavierpsg avatar image
xavierpsg asked

Is it possible to connect 2 inverters together in isolated site: a Victron Energy Multiplusand and a Victron Energy Quattro?

Is it possible to connect 2 inverters together in isolated site: a Victron Energy Multiplus 48/5000 / 70-100 and a Victron Energy Quattro 48/10000 / 140-100 / 100?


If it's possible, what are the connections to make?


Regards


Xavier LEIGNEL

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
kai avatar image
kai answered ·

Parallel systems have to be identical:

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

Can you split your AC distribution in two and run the multiplus and quattro independently?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image
JohnC answered ·

Hi Xavier. Like Kai says.

Thinking outside the square though, the Multi's output applied to one of the AC IN's of the Quattro should give the full 15kVA output of both at the Quattro's OUT's. Interested to hear any 'why-nots' from the worldly who've seen it done..

How the VRM portal deals with that would be fun to see too. :)


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kai avatar image kai ♦ commented ·

i remember seeing something like that on cruiser forums...

found it:

http://www.cruisersforum.com/forums/f14/victron-multiplus-in-parallel-97607.html

so there appears to be at least one functioning system set up like it!

0 Likes 0 ·