question

daaf avatar image
daaf asked

MultiPlus II AC IN

I look for someone to guide me on the adjustment of the Victron Multiplus II 48V/8000VA.
I have almost finished the installation and I am in the first test stage.
THE QUESTION IS:
What parameters of the inverter should I modify, to supply the loads from the batteries when the AC IN is connected to the public network.
When the batteries discharge 50%, the power of the batteries is interrupted,
and LOADS (on AC OUT 1) to connect to the Public Network.
The adjustments will be made with MK3-USB.

Thanks in advance.
PAPPAS Elias

acin
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lex33 avatar image lex33 commented ·
As tu un système GX ? Cerbo multiplus2GX etc
0 Likes 0 ·
Alexandra avatar image Alexandra ♦ commented ·
@Daaf

Ess and a GX (yes the mk3 as well) are needed.

Under ESS on the GX you tell the system ac output not in use


0 Likes 0 ·
3 Answers
Duivert NL avatar image
Duivert NL answered ·

Hi take a look at the ESS manual

https://www.victronenergy.com/media/pg/Energy_Storage_System/en/index-en.html

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lifeingalicia avatar image
lifeingalicia answered ·

Without more details hard to advise.

Be aware the inverter is rated at VA not W - You cant power max load for long. You can restrict the inverter e.g. 5000W, but this also depends on the bat bank and its maximun discharge potential.

Also depending if you use external or internal meter. With the internal meter the inverter will try to power any demand from the battery first before using additional power from the grid if restricted, with an external meter it is the other way round first use grid then ramp up bat supply to match demand or restriction

When you hit SOC no more bat will be used except on grid failure.

See the above mentioned ess manual depending on bat setting the system will increase SOC automatically if you hit it regularly.





2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

w8dev avatar image
w8dev answered ·

Here's a few options: https://youtu.be/4ZsGHi8nKGc

Just a heads up there's some info in the description about something being configured backwards.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.