question

chrigu avatar image
chrigu asked

VM-3P75CT Possibility to daisy-chain on VE.Can

Is it possible to daisy-chain multiple VM-3P75CT trough their VE.Can while only one of them is connected over its Ethernet port to a GX device? Is the GX device able to receive information from all VM-3P75CT in this example?

Would spare the need to install a network switch in the panel if this is possible

vm-3p75ct
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
ldoes (Victron Energy) avatar image
ldoes (Victron Energy) answered ·

Hi @Chrigu, daisy-chaining the VM-3P75CT via VE.CAN is possible, but not in the way you suggest. The units don't aggregate data from each other and therefore one "master" unit will not be able to send data from the VE.CAN network over the ethernet port.

Why not daisy-chain the VE.CAN ports and connect to the GX device via VE.CAN?

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrigu avatar image chrigu commented ·
I have a wireless access point close by that has POE in but also a single ethernet out, means i could use this port.


Using VE.Can directly to the GX device would mean pulling another network cable to the switchboard. But i guess thats the way to go then.


Thanks

0 Likes 0 ·
tk4321 avatar image tk4321 commented ·

Hi @ldoes (Victron Energy),

if I have understood you correctly, two VM-3P75CT (1 x house consumption and 1 x PV inverter), for example, can be connected to the Cerbo GX via single VE.can bus cabling. Both values are then available in the Cerbo GX?

0 Likes 0 ·
ldoes (Victron Energy) avatar image ldoes (Victron Energy) ♦♦ tk4321 commented ·

Hi @TK4321, that's correct. Don't forget to install one of the supplied terminators if the VM-3P75CTs are the last devices in the VE.CAN network.

1 Like 1 ·
tk4321 avatar image tk4321 ldoes (Victron Energy) ♦♦ commented ·

OK, thank you very much.

0 Likes 0 ·