question

smandiol avatar image
smandiol asked

Passtrhu mode stuck and not using solar - 2x parallel Multis II

I have an installation of 2x Multiplus II 5000/48 in parallel, with 3 US5000 Pylontech batteries, plas 2 x smart Solar 250/80 MPPT, and 8.9kWp in solar!

My problem is that with the ESS mode, it gets stuck in ESS#1 and passthru mode in the multis. The thing is, that excess solar energy is not used, neither for load, neither for feeding in the grid.

When I set the ESS to "keep batteries cherged", then the excess soalr energy is used in the correct way.


I´ve seen some discussions about it, but couldn´t find the solution yet.


Here I port some pictures:

1. ESS: "optimized withput battery life" 100% batteries set (just to test), and excess solar is not used.


1718823068921.png


but then, when i switch to "Keep Batteries Charged", then the solar energy excesss is used for loads, and feeding in:

1718823192738.png

Multiplus-IIESSbug report
1718823068921.png (68.4 KiB)
1718823192738.png (63.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

Have you set minimum soc to 100%?

If so. Please just read the manuals and related posts.

(Don’t set 100%!)

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

smandiol avatar image smandiol commented ·
Hi NickDB. I put the value in 95%, 90% and also in 100%. But still do not undesrtand, why it stays so often in Passthru mode, not using solar energy to power the load, nor to feed in excess.


I have read some posts, an also the information is available on the VRM app, and it says that might be due to ESS #1, so BMS does not allow Solar to power the load, but only charge battery... Or I am missing something??


Still not clear...


0 Likes 0 ·
nickdb avatar image nickdb ♦♦ smandiol commented ·
Don’t set the soc minimum above 90%. You have a small battery pack for that setup. If the system can’t properly charge with that config, then your system is imbalanced.
0 Likes 0 ·