I have an installation of 2x Multiplus II 5000/48 in parallel, with 3 US5000 Pylontech batteries, plas 2 x smart Solar 250/80 MPPT, and 8.9kWp in solar!
My problem is that with the ESS mode, it gets stuck in ESS#1 and passthru mode in the multis. The thing is, that excess solar energy is not used, neither for load, neither for feeding in the grid.
When I set the ESS to "keep batteries cherged", then the excess soalr energy is used in the correct way.
I´ve seen some discussions about it, but couldn´t find the solution yet.
Here I port some pictures:
1. ESS: "optimized withput battery life" 100% batteries set (just to test), and excess solar is not used.
but then, when i switch to "Keep Batteries Charged", then the solar energy excesss is used for loads, and feeding in: