Lynx BMS Pre-alarm Disconnect with Cerbo?

Will a system with the Lynx BMS and CerboGX/Touch50 emit an audible alarm before the Lynx contractor is opened? Or does it only alarm after the fact?

Thinking about the case where battery SoC is at 100% but still being charged for some reason, and the BMS is stopping charging for safety. Or the flip side, SoC has reached the minimum threshold (say 10%) and the contractor is opening to preserve remaining power.

lynx bms
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bomax182 avatar image bomax182 commented ·

I found this in the manual:

When the Lynx Smart BMS receives a pre-alarm signal, it will activate its alarm relay and it will generate an alarm message. The alarm message is generated at least 30 seconds before the loads are shut down via the ATD signal.

It suggests that there is indeed a message sent to Cerbo but is not totally clear about it. I suppose I can test this on my system next time I'm at the boat.

0 Likes 0 ·
1 Answer
pwfarnell avatar image
pwfarnell answered ·

The lynx BMS has a pre alarm function that drives a relay in the BMS. You then connect that relay to your own warning light and buzzer because the BMS is often mounted out of the way. The only time this is not available is if you are using the relay to shut down something like an alternator.

See the manual and example schematics available from the downloads on the product page.

https://www.victronenergy.com/battery-management-systems/lynx-smart-bms#manuals

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bomax182 avatar image bomax182 commented ·

What about the case where the Lynx BMS relay is indeed dedicated to alternator control. Will the pre-alarm surface as an alarm on the Cerbo and trigger an audible alarm there?