Looking at a offgrid design in a suburban grid situation using a MultiPlus II or Quattro with a AC coupled Inverter to maximize efficiency and using 3 x 15kw batteries ( design is a work in progress )
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Looking at a offgrid design in a suburban grid situation using a MultiPlus II or Quattro with a AC coupled Inverter to maximize efficiency and using 3 x 15kw batteries ( design is a work in progress )
@s.e.a You have to power all loads from the ACOUT as using ACIN and e.g. ESS requires synchronising with the grid to feed into the household supply to serve the loads. Adjusting the grid setpoint will allow you to control how much and what to do with excess. Not sending excess to the grid in an ESS does not make it off-grid as many wrongly believe.
If you have a cerbo then use the relay output to connect to the Aux of the multiplus.
Program the multiplus to use the general flag to ignore AC in.
Use the generator start stop function of the Cerbo to control the relay
You can then set times for the AC to be activated on the cerbo, this gives you a great deal of control over the input. You can set periodic run times if you want to run it at night for instance, or run it when it reaches a certain SOC. You can also set quiet times to ensure it wont activate during the day when you have sun.