Smart battery protect “output disabled by remote”

img-4613.jpegImage CaptionI’ve scoured this forum and can’t find the answer to why my sbp is stating output disabled by remote. I have it set to lithium ion mode and only have my air conditioner on it. img-4612.jpegImage Caption

img-4614.png

img-4615.png
Battery Protect
img-4612.jpeg (3.3 MiB)
img-4613.jpeg (3.0 MiB)
img-4614.png (142.7 KiB)
img-4615.png (222.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Where is that small blue wire at the remote terminal going to?

This have to be connected to the BMS "load disconnect" (ATD allow-to-discharge) and you also have to connect a positive to the "load disconnect".

https://www.victronenergy.com/media/pg/Lynx_Smart_BMS/en/installation.html#UUID-87790c30-9c19-1d3a-8350-7aee132e1d87

Or you have to connect both remote terminals to the BMS (next schematic in that link)

The ATC and ATD terminals are "dry contacts".

https://www.victronenergy.com/media/pg/Lynx_Smart_BMS/en/installation.html#UUID-d972261e-c728-ee89-eb8e-7c2ed1ef0bb4


Why did you install a SmartShunt? The Lynx BMS already has a Shunt included.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

spamjella avatar image spamjella commented ·

The blue wire is going from the ATD (Terminal 5) on the BMS to H on the SBPn I didn’t realize I needed to also run a positive wire as well from the SBP to the BMS? How would I go about doing that? All the schematics I saw indicated I just needed to run the one wire as I did, I never saw anything about a positive wire going to the ATD port as well.. The smart shunt came with the “box system” I purchased and I’ve been tweaking it ever since.