HI I have a system with a Quattro 15kva and fronius gen plus 5.0 and a generator as the AC input I have used PV assistant and generator start stop and a general flag to ignore ac input.
The issue I am having is when the generator is on during the daytime and if the quattro output is low assume 700Ws, the Fronius trips out and I checked the frequency and it fluctuates from 48.8 to 53Hz which causes the Fronius to trip.
It only happens when the load is low.
The battery was at 48% with 6xUS3000c batteries.
This shows the generator inputting 2kws
At 11.45am the fronius drops to 0 with High Frequency fault
The frequency Jumps upto 53.1hz which affects the fronius to trip. Ignore the frequency fluctuations before 9.30am, it was because of the pv assistant configured wrong.