Why is ACin2 powered when ACin1 is connected with quattro 24/3000?

why do I have a voltage on the quattro 3000 with "ac 2 in" when shorepower is connected to "ac1 in"? There are no assistants or relay enabled.

MultiPlus Quattro Inverter Charger
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

050560 avatar image 050560 commented ·


There are 230V on the AC IN2. Does anybody knows why?

0 Likes 0 ·
img-4541.jpg (373.7 KiB)
1 Answer
Margreet Leeftink (Victron Energy Staff) avatar image
Margreet Leeftink (Victron Energy Staff) answered ·

This should not be normally the case. when AC 1 is in use, AC 2 should be disconnected. See below internal wiring diagram of the Quattro.


Test to be done by licensed electrician:

Test by disconnecting the ACin-2 wires and all the AC out wires. Turn ACin-1 on, wait until the Quattro starts charging and then test the ACin-2 terminal. If a mains voltage is measured on the ACin-2 terminal then please get in touch with your Victron distributor for further advice.