How do I limit battery charge current. With DVCC - MPPT will not be reduced.

Background - in good days with enough PV yield the battery is full at midday. Then the MPPT is throttled. We want to load the battery slower over the whole day and use the sureplus power for heating water or grid feed in.
How can achieve this- normaly i think with DVCC - but the GX manual 11.4.6 says that this wouldn't be appylied to MPPTs.
I tried it with nodered

MPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
jetlag avatar image
jetlag answered ·

Do you have the option "DC-coupled PV - feed in excess" activated? If yes, then the DVCC will not work for the MPPT.


See also this link:

ESS manual - DC-coupled PV - feed in excess - incorrect information?