Orion dc to dc isolated vs non

Ok, converting my bank of 6- trojan t-105's to 2- 300AH LiFePO4. Obviously concerned with my alternator (70amp) output that currently goes to the Trojan bank. Because my Start battery (AGM) and Gen battery (AGM) are maintained by Blueseas ACR's from the house bank, will an Orion dc to dc 30amp non isolated from the alternator to the lithium bank work?

orion dc-dc
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alistair Warburton avatar image
Alistair Warburton answered ·

Personally I would always opt for an isolated unit, because it is safe in all 'non-silly' situations. Obviously non isolated units are cheaper and perfectly adequate in many circumstances.

Can you post a diagram? has everything got a common ground/neg now?

That said ... I don't know if bridging the Neg of an isolated unit could cause an issue... It shouldn't, but I guess that is an equally valid question if the unit is trying to do anything clever with insulation monitoring.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
No issue bridging the negs. Except you lose the isolation.