Hi, i have a 20kW Fronius symo and 8kW fronius inverter symo, both are 3-phase system. Can i daisy the 2 system with different capacity and couple their output with the output of 3 units of 15kva quattro inverter?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi, i have a 20kW Fronius symo and 8kW fronius inverter symo, both are 3-phase system. Can i daisy the 2 system with different capacity and couple their output with the output of 3 units of 15kva quattro inverter?
What do you mean with Daisy Chain?
If you have 3 Quatros with total 45kVA/36kW and only 28kW Fronus Symo, simply connect the ACout of the Quatros and the ACout of the two Fronius SYMO to the BusBar.
Do not forget in the Quatro the option "has PV" and setup the shifting Frequency correct.
Hi Konzack, the system has been set up and is operational. Find attached the screenshot of the Cerbo GX and VRM of the installation. Screenshot_20240521_125833_VRM.jpg 20240521_103009.jpg