Why did you change the Victron & Pylontech manual?

Dear @Daniël Boekel (Victron Energy Staff)


Recently I noticed that you changed the DC input disconnect voltage to 44V

LINK VICTRON LIVE

Pylontech manual says limit discharge voltage is 44,5V

Would it be safe? Why did you make this change?


Best wishes,


Daniel.

Pylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Daniel Toribio

This was done to prevent unnecessary 'low voltage' warnings and -alarms

Also, the system will stop inverting when the battery gives a DCL=0 message


btw. when using ESS, the values are 46 volt shutdown and 47,2 volt restart, so the numbers I changed are only used for off-grid normally, where the old numbers gave some unwanted effects (not starting up the inverter while battery was at 50% SOC)

When in the feature the shutdown / restart voltage can be configured closer to each other, these numbers will be changed again.