Dear @Daniël Boekel (Victron Energy Staff)
Recently I noticed that you changed the DC input disconnect voltage to 44V
Pylontech manual says limit discharge voltage is 44,5V
Would it be safe? Why did you make this change?
Best wishes,
Daniel.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Dear @Daniël Boekel (Victron Energy Staff)
Recently I noticed that you changed the DC input disconnect voltage to 44V
Pylontech manual says limit discharge voltage is 44,5V
Would it be safe? Why did you make this change?
Best wishes,
Daniel.
This was done to prevent unnecessary 'low voltage' warnings and -alarms
Also, the system will stop inverting when the battery gives a DCL=0 message
btw. when using ESS, the values are 46 volt shutdown and 47,2 volt restart, so the numbers I changed are only used for off-grid normally, where the old numbers gave some unwanted effects (not starting up the inverter while battery was at 50% SOC)
When in the feature the shutdown / restart voltage can be configured closer to each other, these numbers will be changed again.