Hi There!
I have a:
SmartSolar 150/70
SmartSolar 100/20
SmartShunt 500A
I run a consistent load of 11A via a non-victron inverter.
The MPPTs, and load are connected to the battery via the shunt.
All devices are on the same VE.Smart network (Bluetooth), and are within 1m of each other.
Due to the characteristics of my battery, I run a fairly low bulk/absorption voltage, and use a tail current of 5A to terminate absorption.
This has been working well until the last time I performed a firmware update.
since the update, one MPPT in the smart network (not necessarily the same one each time) does not end its absorption when the tail current reaches 5A, and instead continues in absorption for the full time limit set, while the other one patiently waits in float.
If I remove one of the MPPTs from the smart network, everything works as expected.
So, this appears to be a problem with Syncronised charging not working correctly within a bluetooth smart network. Current sence received from the shunt is not being communicated properly between the MPPTs,
Any ideas?