Can the Lynx shunt handle 3xMultiplus 15000

Hi Guys.


I want 900A to go over the busbars. But there is No 900A or 1000A fuse for the shunt.

Why is this? If its ratet for 1000A?

There are six batterypacks with 150A on one Side of the shunt and 3 x Multiplus 15000 on the other Side.

Is this Safe?


Thanks

lynx shuntcurrent limitlynx distributorsafety
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Max insel

Fuse each individual item to the bus bar. Then the fuses are more reasonable and everything is still protected.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

max-insel avatar image
max-insel answered ·

Thanks

Yes i will fuse each Item. But i'd Like to have the Lynx shunt in between the battery and the Multiplus. And for that some Kind of Connection is required in the shunt.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.