Connect a Multiplus 3000 to Cerbo-S GX

From reading the manual for my new MultiPlus 12-Volt 3000VA 
120 Amp 120V, I see that there are two RJ-45 ports described as: "2x RJ45 connector for remote panel and/or parallel and 3-phase operation."

Do I connect one of these to the VE.Bus on the Cerbo-S GX? Does this use a standard Ethernet cable?

TIA,

Eric


cerbo gxmultiplus ve.bus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Kevin Windrem avatar image
Kevin Windrem answered ·

Yes. The two RJ-45s are simply in parallel so it does not make any difference which one is connected to Cerbo.

The connectors allow multiple VE.Bus devices to be connected to the same bus. For example if you have a parallel or 2/3-phase Multi system.