I've seen some similar posts to this issue but no resolution yet. So, here is my case:
I have a fresh victron installation at my boat. Multiplus 1600/35, Lynx Shunt, MPPT and a cerbo gx for configuration and monitoring.
I installed and configured 3 temp inputs (original victron sensors) and an existing tank sensor (EU setting).
All worked fine for some weeks. Then I had a low voltage situation (about 11.3V). The system rebooted and since that point does not show any analog I/O. It is complete missing in the configuration items.
The battery protect had disconnected all loads before that time. The cerbo was not disconnected, it uses a direct circuit.
Other Bluetooth based sensors still work fine, only analog is missing.
Original setup was done with OS V 3.13.
Things I tried to restore the analog inputs:
- Reboot happened at V 3.20
- disconnect and reconnect analog sensors - no change
- Update to V 3.31 - no change
- Update to V 3.40 -10 (beta) - no change
- Power down 10 Minutes - no change
My next attempt would be a reset to delivery settings, which I'd like to avoid if I could.
Any ideas?
I have some stale feelings here, as I rely on these inputs (fuel capacity, temp for ventilation activation, ...). A configuration has to survive a low voltage situation!