robertg asked

SKYLLA- TG 24/50 3- Phase REM function

Hi. Can anyone provide some information about the remote function (REM) on a SKYLLA- TG 24/50 3- Phase charger?

We need to install a remote ON/OFF function on a charger built into an existing system. We can't access the charger until the job is actually done, and even then access will be difficult and time limited, so we need to get it right first time. It can't be tested until the system is rebuilt, and it will have to be stripped again to make changes which is a big job, so you can see my problem.

The user manual (Manual-TI01170-EN - 4.12, p23) is quite vague about exactly how REM functions. The manual instructs us to connect a remote switch between REM and GND but it doesn't tell us what happens when the switch contact is made. Does connecting REM to GND enable or disable the charger? Sorry if this seems very trivial but we want to be 100% sure as it will involve a relay and PLC software on top of the access problems.

Thank you.

Skyllaskylla tg
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi Rob,

You will receive an answer very shortly.

0 Likes 0 ·
1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

If REM is connected to GND then the charger switches OFF.

Open circuit voltage is 5V.

Short-circuit current from REM to GND is 1mA