Multiplus replacement with VE.Net Blue Power Panel

Hi,


I'm replacing a faulty 3kw Multiplus in an existing setup based on VE.Net


The panel being used was a Blue Power Panel (not sure if it's a v1 or v2 - the system was built in 2012).


The problem I have is that, despite having reconfigured the Multiplus with VEConfigure - the panel still show the connection with it in "Initialising" forever.


Any help please?


Thanks in advance

blue power panelVE.Net
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

7 Answers
Martijn Coster (Victron Energy Staff) avatar image
Martijn Coster (Victron Energy Staff) answered ·

@stepir For it to work with the latest Multi firmware the VVC needs to be 0x0402. It is not possible to update this firmware yourself. A special programmer is needed. You could try changing the firmware of the Multi 143 if you are not planning on using assistants. If you want to use assistants then it would be best to upgrade to a ColorControl and a BMV
Fot this it would be best to contact your distributor

best regards

Martijn Coster - Victron Energy

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stepir avatar image stepir commented ·

THANKS!!!!

0 Likes 0 ·
Martijn Coster (Victron Energy Staff) avatar image
Martijn Coster (Victron Energy Staff) answered ·

@stepir Do you know which firmware the old Multi had? What firmware does the new Multi have? 4xx?
The problem is probably that the BPP needs a firmware update to work with a Multi with the latest firmware. If it is a v1 BPP a firmware update is not possible.

Advice would be to replace the BPP for a CCGX. But when more VENet is used that will not be an option

best regards
Martijn Coster - Victron Energy

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stepir avatar image
stepir answered ·

Hey Martijn!


Thanks!


The old one was using 1909143 so it's substantially a different machine compared to the new one.


Replacing the panel would be odd as the customer is not expecting it - the multiplus have only be replaced as it was faulty.


Also the rest of the setup is still using some VE.Net accessories - the battery monitor in example - meaning he will have to buy and install also a BMV...

I believe it's a BPP v1 - how can i check? externally they seems identical?


Thanks again

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stepir avatar image
stepir answered ·

img-0369.jpg (3.9 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Martijn Coster (Victron Energy Staff) avatar image
Martijn Coster (Victron Energy Staff) answered ·

@stepir Can you go into the menu and look up the firmware versions?
In the Multi menu and then all the way down it should say VVC Version.
And in Local settings somewhere in the middle it shows Software version. That will determine the model.
Best regards
Martijn Coster - Victron Energy

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stepir avatar image
stepir answered ·

@Martijn Coster (Victron Energy Staff) Software version 0x0107 - VVC version 0x0300

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stepir avatar image
stepir answered ·

Hey @Martijn

just to confirm: I've loaded this morning FW 150 (w/o assistants support) and then everything got back working!! thanks again and happy holidays from Italy!

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Thanks for letting us know everything is working great now

0 Likes 0 ·