Need a quick sanity check on the version of ET340 that supports US split phase (120v/240v).
Victron manual states that the following version is supported & for sale through them: EM24DINAV53DISX
When you look at the actual Carlo spec sheet the voltage ranges do not line up for split phase market.
AV5: 400VLL AC - 1/5 (10)A (CT connection) VLN : 160 V to 480VLN VLL : 277 V to 830VLL
AV2: 400VLLAC 10(65)A (direct connection) VLN : 113V to 265VLN VLL : 196V to 460VLL
I believe for split phase AV2 is needed - spec. sheet (linked to a reseller since the manufacture site is tough to navigate)
Accurate or am I misreading the sheet?
In addition I can find the AV5 for sale but not AV2 and I would need to use a CT sensor and AV2 appear to only support a shunt.
Anyone using the ET340 successfully in a 120/240V setup and measuring up to 65amps? If so what version and what is your setup?
Thanks