Power from PV inverter connected to Multiplus AC IN not used

Hi

I would like to have some thoughts on this issue:

I have the following setup:

Multiplus with Generic PV inverter connected to the AC IN of 2 x 3kVa Multi and SMA SunnyBoy Connected to the AC OUT of the Multis. The Generic PV inverter connected to the AC IN is being monitored by the victron current sensor: https://www.victronenergy.com/meters-and-sensors/ac-current-sensor

For some reason, victron is not using the power generated by the generic PV inverter connected to the AC IN of the Multi, this power is just being feed into the grid:

1713261243733.png

And it seems like the Generic PV inverter is setup correctly:
1713261265450.png

1713261286773.png




AC PV Coupling
1713261243733.png (35.4 KiB)
1713261265450.png (27.2 KiB)
1713261286773.png (23.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Mopanie

It is more like it is not being considered at all.

If I just do basic maths on the tiles screen....

(3,058+661)-(1,597+1,475)=647 remove 70w for system consumption - 577 to grid.


How is it connected to the system?

How is it configured on the GX?

I haven't used one personally but does it have a CT direction as well?