Hey,
I've already asked in the German-speaking area, but unfortunately I haven't received an answer yet. :-(
So, here in English:
I've had an "EV Charging Station NS" in my Victron setting for a few days.
I control the entire system with IP Symcon and Modbus. I have already converted the EVCS to switch between 1 - 3 phases. (official modification)
There are some parameters in the Modbus Excel list that I don't understand. - Currently I am not satisfied with the steps (increasing / decreasing the charging power of the speed it changes these values of the EV charger). Sometimes it moves up too quickly and then has to reduce the power again sharply.
I would like to optimize the steps and timing.
Can someone please help and explain the following parameters?
| 5057 | Power for 3phase | uint16 | 1 to 65535 | 4800 | R/W | yes | W. Related to 'multiple relay charging' feature. |
| 5058 | Power for single phase | uint16 | 1 to 65535 | 4300 | R/W | yes | W. Related to 'multiple relay charging' feature. |
| 5059 | Phase switching timeout | uint16 | 1 to 65535 | 60 | R/W | yes | s. Related to 'multiple relay charging' feature. |
| 5068 | Backup battery emulation | uint16 | 0 to 1 | 0 | R/W | yes | 0 - disabled, 1 - enabled |
| 5069 | 'Feed in'. Start delay | uint16 | 1 to 65535 | 30 | R/W | yes | s |
| 5070 | 'Feed in'. Stop delay | uint16 | 1 to 65535 | 60 | R/W | yes | s |
| 5071 | 'Feed in'. Single phase. Grid power for start | int16 | -32768 to +32767 | -500 | R/W | yes | W |
| 5072 | 'Feed in'. Multi phase. Grid power for start | int16 | -32768 to +32767 | -1400 | R/W | yes | W |
| 5073 | 'Feed in'. Grid power threshold for increase | int16 | -32768 to +32767 | -250 | R/W | yes | W |
| 5074 | 'Feed in'. Grid power threshold for decrease | int16 | -32768 to +32767 | 250 | R/W | yes | W |
| 5075 | 'Feed in'. Backup battery discharging power threshold | int16 | -32768 to +32767 | -100 | R/W | yes | W |
| 5076 | 'Feed in'. Current step | uint16 | 1 to 65535 | 2 | R/W | yes | A*10 |
| 5077 | 'Feed in'. Time step | uint16 | 1 to 65535 | 1000 | R/W | yes | ms |
| 5078 | 'Battery powered'. Start delay min | uint16 | 1 to 65535 | 30 | R/W | yes | s |
| 5079 | 'Battery powered'. Stop delay | uint16 | 1 to 65535 | 60 | R/W | yes | s |
| 5080 | 'Battery powered'. Start abort delay | uint16 | 1 to 65535 | 10 | R/W | yes | s |
| 5081 | 'Battery powered'. BKPB balance power | uint16 | 0 to 65535 | 500 | R/W | yes | W |
| 5082 | 'Battery powered'. BKPB balance SOC max | uint16 | 1 - 100 | 98 | R/W | yes | % |
| 5083 | 'Battery powered'. Available sun power threshold for start | uint16 | 0 to 65535 | 100 | R/W | yes | W |
| 5084 | 'Battery powered'. Grid power threshold for start | uint16 | 0 to 65535 | 25 | R/W | yes | W |
| 5085 | 'Battery powered'. BKPB power threshold for decrease | uint16 | 1 to 65535 | 250 | R/W | yes | W |
| 5086 | 'Battery powered'. Grid power threshold for decrease | uint16 | 1 to 65535 | 250 | R/W | yes | W |
| 5087 | 'Battery powered'. Discharging detect timeout | uint16 | 1 to 65535 | 7 | R/W | yes | s |
| 5088 | 'Battery powered'. Next try timeout for increase | uint16 | 1 to 65535 | 45 | R/W | yes | s |
| 5089 | 'Battery powered'. Time step | uint16 | 1 to 65535 | 15 | R/W | yes | s |
| 5090 | 'Battery powered'. Current step | uint16 | 1 to 65535 | 10 | R/W | yes | A*10 |
| 5091 | 'Battery powered'. Grid power for 'feed in' detection | int16 | -32768 to -1 | -100 | R/W | yes | W |
| 5092 | 'Battery powered'. Start delay max | uint16 | 1 to 65535 | 180 | R/W | yes | s |
| 5093 | ON grid detection threshold | uint16 | 0 to 65535 | 0 | R/W | yes | W |
What exactly is "Feed in" and "Battery powered"?
I hope someone can help me.
Thank you, Martin