ESS, single Multi in 3 phase system and no grid feedback

Hello! In a setup where grid feedback is not allowed, is it possible to have a single Multiplus or Multiplus II or similar installed on a single phase of a 3 phase network (230V), while having all or most of ESS features ? Will ESS phase compensation be possible without being able to feedback to the grid? If not, is this an issue? Many thanks!

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Jaco Reinecke avatar image
Jaco Reinecke answered ·

Hi,

Yes, you can set ESS to not feed back. By running Optimized with Battery Life, you can set the Grid Setpoint. The higher that value is, the less it will feed back, bar when a large load is switched off. Then some current will be fed back but that should not be a problem.

Hope this helps.

Regards
Jaco

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ramin avatar image ramin commented ·

Thanks for your reply. How about the phase compensation feature, does it require grid feedback ? It seems it will need so to balance all 3 phases but I am not certain.

Thanks!

0 Likes 0 ·